Thread: Voltage Drop Calculation

  1. #1
    Join Date
    Dec 2020
    Posts
    42
    Post Thanks / Like

    Default Voltage Drop Calculation

    I am trying to calculate voltage drop given a wire gauge, wire length and ampere current. I've found several calculators, but they seem to be giving different results. For example, assume:
    One-way wire length: 30'
    Amps: 3A
    Wire: 16AWG

    http://wiresizecalculator.net/calcul...oltagedrop.htm
    Voltage Drop:0.9V

    https://www.calculator.net/voltage-d...feet&amperes=3
    Voltage Drop: 0.72V

    It seems the first link is using the formula:
    2 * K * L * I / Cm
    K = ohms-cmil per ft - 12.9 for copper
    I = current (or amperes) of load
    L = length of conductor in ft. (one-way)
    cmil = circular mil area of the conductor

    https://www.rpc.com.au/pdf/Wire_Chart.pdf


    Whereas the second is using: 2 * L * I * R / A
    L = one-way length
    I = amps
    R = resistance of cable - 0.017 for copper
    A = cross sectional area of cable in (mm˛)

    http://www.adamselectric.coop/wp-con...ltage-Drop.pdf


    What formula is correct in the context of pixels and this hobby?

    Thanks,
    - pc

  2. #2
    Join Date
    Aug 2012
    Location
    Nova Scotia, Canada
    Posts
    1,829
    Post Thanks / Like

    Default Re: Voltage Drop Calculation

    Go here: http://spikerlights.com/calcpower.aspx
    Works a treat and helps a ton to get a rough estimate to help plan out display.
    Phil

  3. #3
    Join Date
    May 2007
    Posts
    5,465
    Post Thanks / Like

    Default Re: Voltage Drop Calculation

    Without having looked into it in detail, I suspect that what you noticed may be due to the difference between using 60 Hz AC RMS voltages (and RMS currents) vs DC voltages.
    Phil

  4. #4
    Join Date
    Nov 2019
    Location
    Edmonton
    Posts
    129
    Post Thanks / Like

    Default Re: Voltage Drop Calculation

    You can obtain the approximate resistance per foot (meter) of AWG copper wire on the wikipedia page here: https://en.wikipedia.org/wiki/American_wire_gauge

    V = I * R

    Remember, your total conductor length is the length of the V+ wire plus the length of the GND wire. That is why there is a "2" multiplier in those examples you provided.
    Last edited by steve123; 02-07-2021 at 07:04 PM.

  5. #5
    Join Date
    May 2007
    Posts
    5,465
    Post Thanks / Like

    Default Re: Voltage Drop Calculation

    Quote Originally Posted by P. Short View Post
    Without having looked into it in detail, I suspect that what you noticed may be due to the difference between using 60 Hz AC RMS voltages (and RMS currents) vs DC voltages.
    I was thinking of skin effect, which is negligible for wire of that diameter. Instead, if you look at the text for the first calculator mentioned, it's for a temperature of 75C. The resistance of copper increases with temperature, which accounts for the difference in voltage drop between the two calculators. From what I could find on that most wonderful of sources, the internet, the resistance of copper increases by 0.393% per degree C. The temperature difference is 55C, so the resistance increases by a factor of (1.00393^55) = 1.24, and 0.72V * 1.24 = 0.89V (approximately the numbers given by the two calculators).
    Phil

  6. #6
    Join Date
    Dec 2020
    Posts
    42
    Post Thanks / Like

    Default Re: Voltage Drop Calculation

    Thank you Phil - I didn't notice that distinction. I also now see the two formulas are really the same, albeit one is imperial and the other metric.